Which caps should I use for power conditioner? I red about X, 2X and Y rated caps. Are they interchangeable for PC? Does any one know polypropylene caps I could use for PC? If yes digikey or mouser parts preferable but not necessary. I tryed to search but cann't find right thead.
 
X & Y caps are for connecting direct to the mains.
X2 connect live to neutral (hot to cold?)
Y connect live to earth and neutral to earth (hot or cold to ground?)
Keep the earth caps (Y) smaller to reduce earth leakage, try 10nF to 47nF.
A few 3 terminal Y caps are available to connect across all three poles of a single phase supply (live/neutral/earth).
 
Hi,
thanks for confirming that calculation.
An RCCB (rcd) protected circuit should have an operating earth leakage current NOT exceeding 25% of the rated trip current of the breaker.
Normal domestic mains protection usually use a 30mA RCCB.
Maximum operating leakage would therefore be 7.5mA.
A 4n7F cap from live to earth will transfer 0.354mA (50Hz & 240Vac) to earth.
This allows a further factor of safety in excess of 21.
I recommend a sensible limit for the Y cap to earth of 10nF to 47nF. This cap range would allow multiple appliances on the protected circuit using upto about 100nF total capacitance to earth and stay below the recommended 25% limit.
 