I have 3 Amveco toroids, but Amveco won't tell me what the wire color codes are because these toroids were custom made and do not disclosed this info to 3rd parties.
What's a safe way to test toroid transformer secondaries not connected to a circuit? It has several secondary taps. It can be wired as 28v or 15v at 4.67 amps.
I want to wire it for low volts and high current, but not sure what wire goes where.
Thanks,
Vince
What's a safe way to test toroid transformer secondaries not connected to a circuit? It has several secondary taps. It can be wired as 28v or 15v at 4.67 amps.
I want to wire it for low volts and high current, but not sure what wire goes where.
Thanks,
Vince
First, use your ohmmeter to find what's connected to what, and draw a wiring diagram.
Then, run a low voltage to the primaries. You can use a spare amp to feed it, for example 60Hz 12V (or whatever is one tenth of your outlet voltage), then multiply your secondary voltage readings by 10.
Then, run a low voltage to the primaries. You can use a spare amp to feed it, for example 60Hz 12V (or whatever is one tenth of your outlet voltage), then multiply your secondary voltage readings by 10.
vdi_nenna said:I want to wire it for low volts and high current, but not sure what wire goes where.
Remember that only identical secondaries can (effectively) be wired in parallel.
Remember that only identical secondaries can (effectively) be wired in parallel.
That's what I'm worried about.
I usually use a function generator. Fairly low current output, so no danger at all. Might not be the best for very large toroids though.
Failing that (as I don't always have access to a function generator), I just do what jnb said and use an amp to power it with a 60Hz test tone.
Failing that (as I don't always have access to a function generator), I just do what jnb said and use an amp to power it with a 60Hz test tone.