Hi all
I would like your advise on the proper way to wire the secondary of an isolation transformer, so as not to violate the electrical safety of the equipment to be connected to it ( audio gear) and to retain - as much as possible - the isolation from the noise which is superimposed on mains wiring. I spent a few hours reading books and some more hours on the internet, but the opinions are really conflicting. Attached is a sketching of 3 different connections. Please commend Best Regards George |
|
|
|
|
#2 |
|
Did it Himself
diyAudio Member
|
1
2 is bad 3 is dangerous
__________________
www.readresearch.co.uk my website for UK diy audio people - designs, PCBs, kits and more |
|
|
|
|
#3 |
|
diyAudio Member
Join Date: Oct 2006
|
Why are 2 and 3 not equivalent ? They are both labelled E, yes? Or are you saying the output end of E is not bonded to the panel earthing conductor? It must be, no exceptions.
With very rare exceptions, 2 is the only legal method (in the USA) if you are feeding multiple equipments with this power supply. If it is only being used inside a single enclosure, then 1 can work. However, it is typically a good idea to earth the equipment at some point, even if through a resistor. A completely floating supply has its own set of problems. What do you intend on this supply feeding, specifically? |
|
|
|
|
#4 |
|
diyAudio Member
Join Date: Nov 2002
Location: Athens-Greece
|
Zigzagflux
I intend to use such an isolation transformer (IT) to feed the pre-amp, main amp, tuner and CD drive . Richie00boy In fact the wiring per sketch No 1 is the way that any step-up or step-down transformer is wired in any linear PSU I have an isolation transformer (IT) in my lab, which is wired as in the No 1 sketch. I use it during repairing equipment for reducing the likelihood of becoming a spirit. So far so good. But today morning during some mains noise monitoring, I thought of measuring the noise at the output of this IT. Then to my surprise, I noticed that the voltages of the thus wired secondary were behaving quite strangely (strangely to me). See attached photo. Is it normal? Is it safe? When the secondary is wired as per No 2 and No 3 sketches, voltages are as on the primary. No surprise. Regards George |
|
|
|
|
#5 |
|
diyAudio Member
Join Date: Sep 2006
Location: Mar del Plata, a BIG seasonal getaway city, can see the Ocean from our residence.
|
I would bet the wiring of the output of your IT is currently correct. Did you notice your measurements on the secondary don't add up to your 229Vac?
Think how the circuit works as in electron flow. The measurements from Live or Nuetral to Earth are capacitatively(?) coupled...I think that your DVOM puts such a light load on the circuit...that you can get any reading. I would bet if you loaded the circuit just a little you won't read any voltage at all. Wouldn't be baffling if you had a cheap meter & you tested both 'L' & 'N' ...and it gave you no readable voltage? You should be able to pull down that reading with microamps & the voltage would drop.to nothing. As has been said over & over, rectifying AC from the wall is dangerous because the live side to earth AND/OR Nuetral is hot. Thats my take on it....I'm probably wrong in my assumptions, but.... ___________________________________________Rick... .......... |
|
|
|
|
#6 | |
|
diyAudio Member
Join Date: Oct 2006
|
Quote:
I am not sure where the idea came from that a completely isolated system is the ultimate goal, but it's not. Ungrounded systems are prone to transient overvoltages and nondesirable capacitive coupling effects (which is why the Code limits their use). If the transformer was exclusively used inside one single component, such as your amplifier, then you are able to leave it isolated (or resistance grounded as mentioned above). This is found in section 450, IIRC. Section 640 addresses some specific allowances for audio equipment, but there is no allowance for isolated systems feeding a power strip to multiple devices. Others can debate the pros and cons of grounding the secondary from an audible standpoint; but sorry to say, legally it must be grounded. I am open to someone showing me a Code exception that I have missed (they are very easy to miss). |
|
|
|
|
|
#7 |
|
diyAudio Moderator
Join Date: Oct 2007
Location: Santa Cruz, California
|
Yes, earth must be earth. /Do not defeat your safety ground!
The strange readings you get are as Richard Ellis alluded. The uA leakage currents flowing through your voltmeter are causing an AC voltage to be read. It's an artifact because the secondary if floating. The requirement to tie neutral to earth is only at the power panel. Never do this anywhere else. The key reason to use an isolation transformer is to protect yourself from live chassis. If you are holding a grounded (earthed) pipe for instance and touch a live chassis, the isolation transformer will prevent electric shock. You'll still get a tingle from the leakage current but it won;t stop you heart. Remember power engineering 101 - keep one hand in pocket! To filter noise from the mains, you're better off with filters to target the band of interest: common mode chokes, small properly rated caps. Toroids have high bandwidth and couple a lot of cr@p. E-I iron laminated cores are pretty narrow bandwidth and help. The interwinding screen (faraday shield) only stops common mode capacitively coupled noise, not the predominant dirty sine + RF that usually comes out the wall |
|
|
|
|
#8 | |
|
diyAudio Member
Join Date: Dec 2008
Location: Victoria, BC
|
Quote:
There won't be appreciable current flowing between the isolated 'live' and the earth connection. So, once we have moved the isolated supply off the chassis with the possibility of accidental connection to the live mains (not isolated) circuit, what's the point of the earth conductor? It seems to me that you are really dealing with a two-conductor, isolated system which is not referenced to ground (or neutral). So once you are on the isolated side of the transformer, you need to pay attention to the fusing arrangement, since you can no longer depend on the main breaker/fuse for protection. In spite of code 'requirements', isn't the earth really just a decoration after the isolation transformer? BTW, there is a lot of info on this topic in marine wiring systems, where isolating the boat from the electric currents flowing around the marina can be a big deal. Slightly (or more) baffled, John |
|
|
|
|
|
#9 | |
|
diyAudio Member
Join Date: Oct 2006
|
Quote:
|
|
|
|
|
|
#10 |
|
diyAudio Moderator
Join Date: Oct 2007
Location: Santa Cruz, California
|
This is good, we have a quorum of experience.
Regarding safety ground on the isolated side. I will clarify my point by saying that safety ground is a fundamental protection for persons who may come into contact with the equipment. In the event of an IT pri-sec short, safety ground will still protect the casual user. What you do in the private of your own lab is your own concern zigzagflux: If you enforce the neutral-ground tie on the isolated side, then there must be some requirement to maintain polarity right? It sounds like you have experience in the power industry that I/we can learn from. Can you give us some more info? |
|
|
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
|
|
|
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Isolation Transformer question | Jack Torrance | Power Supplies | 7 | 2nd January 2007 08:37 AM |
| What if you wire an isolation transformer like so? | leadbelly | Power Supplies | 4 | 29th January 2006 02:21 AM |
| New To Site? | Need Help? |
| Page generated in 0.14344 seconds (86.16% PHP - 13.84% MySQL) with 11 queries |