Limiting inrush to a variac.

I have 15A 240V variac, and I want to limit the inrush current. It seems an NTC thermistor is a simple way to do this. Unfortunately I am even simpler than the calculations needed!
At the moment there is nothing connected to it, but it could be used for powering a large Japanese 100V amp.
So, any help would be welcome.
 
This is a very interesting subject, and I look forward to the exchanges here.

I have a variable transformer, and whenever I turn it on for the first time (even with output knob all the way down), it always trips my 15A home breaker. Once I reset the breaker and turn on the transformer, it works as normal. I rarely use the transformer so months may pass between uses. I am speculating that the magnetic core of the transformer is unmagnetized after long periods of disuse, and turn-on causes a surge that trips the house breaker.
 
  • Like
Reactions: rayma
1500 VA variable transformer, bought new from Marlin P. Jones. Works well, no vibration or hum when in use. Just sets off the breaker, that is all.

Breaker is a GE, as I recall, but it could be another name brand breaker. Never had problem with the breaker (I run my soldering iron, lights, and Milwaukee battery charger on the same circuit (not all at once in fact nothing else is on the breaker when using the transformer) EXCEPT when for first turn-on of transformer. Hence, I think the breaker is not the problem.
 
@awkwardbydesign

When you say "Japanese 100V amp", do you mean it's a 120 VAC mains voltage version, Accuphase have a few mains voltage versions for different markets, the other two are 220 VAC and 230 VAC according to the PDF, link below.
https://www.accuphase.com/model/e-480.html
https://www.accuphase.com/cat/e-480_e.pdf
https://web.archive.org/web/20220000000000*/https://www.accuphase.com/cat/e-480_e.pdf

As for NTC's as inrush limiter for your variac, which can be treated as a transformer of the same kVA rating, you may have a look at the two article links below, the links takes you directly down to the relevant text discussing NTC's pertaining to your case.
In short it's not at all recommended to use an NTC and in particular when the load is not constant, such as a power amps like the Accuphase which datasheet says: "Power Consumption 93 watts idle, 425 watts in accordance with IEC 60065", (exceptions would in mostcases be for class-A amps).
https://sound-au.com/articles/soft-start.htm#s3
https://sound-au.com/articles/inrush.htm#s61

If you look around at that site you will find other types of inrush limiters, but a one single component solution there are not, if you need just a temporary solution it's best to add a suitable resistor in series with the variac and a switch to bypass the resistor, the inrush current spike is usually decaying away within the first couple of seconds.
 
Last edited:
the same position
Your wall-outlet can surely support 16 Amps? In the listings and data linked just above, the maximum max current listed is 12 Amps.

Model Number - R25 - Max.Current (A) - Approx. Resistance in Max. Current at 25
NTC0R7D-20 ----0.7 --12 --------------- 0.018

Since your actual load "large amp" is under 3Amps @ 240V, you could even use NTC20D-15, 20r, 4A. The peak current is 240V/20r or 12 Amps.

Of course a fixed autotransformer is a better bet for steady use. The cat can't bump it from 100V to 189V. The EI core has less surge. It saves a lot of iron.
 
Maybe try an isolation transformer between the variac and the wall, you know the 1:1 things that are used for power conditioning? That way there's two cores that need energizing.
 

Attachments

  • IMG_8109.jpg
    IMG_8109.jpg
    392.2 KB · Views: 87
Your wall-outlet can surely support 16 Amps? In the listings and data linked just above, the maximum max current listed is 12 Amps.

Model Number - R25 - Max.Current (A) - Approx. Resistance in Max. Current at 25
NTC0R7D-20 ----0.7 --12 --------------- 0.018

Since your actual load "large amp" is under 3Amps @ 240V, you could even use NTC20D-15, 20r, 4A. The peak current is 240V/20r or 12 Amps.

Of course a fixed autotransformer is a better bet for steady use. The cat can't bump it from 100V to 189V. The EI core has less surge. It saves a lot of iron.
The "large amp" is just an early example. I could be using two monoblocks, plus preamp plus CD player if I can afford them. And generally they would be turned on after the variac.
 
For laboratory use: connect a 150 watt incandescent light bulb in series between the mains and the variac. Connect a household SPDT light switch in parallel with the bulb.

Before turn-on: set the SPDT switch to its open circuit ("off") position

At turn-on: apply AC mains to the series assembly. The light bulb glows and limits the inrush current to a value less than or equal to (150W / MainsRMSvoltsge) amperes.

1 second after turn-on: the inrush event is over, the variac's sinusoidal voltage waveform and sinusoidal current waveform are now in their proper phase, so it is now time to close the SPDT switch ("on" position) and short out the light bulb. Now the variac is connected directly to the AC mains.