UK AC Mains voltage?

Is there any confirmation that the U.K. is now supplying 230v or is it still at 240v?

I thought that some years ago it was going to be dropped down to 230v with a tolerance of +10% -6% ?

So the 230v could be 230v + 23 = 253v

or 230v - 13.8v = 216.2v
 
Last edited:
So the 240v can fluctuate anything from 240v up to 253/4v.
Although it 'might' be the case that some devices can handle the higher voltage but what happens to those devices that can't.... shortened life?
European devices are sold for 220/230v....... and many of these devices are sold in the U.K.
 
I thought (my memory is fuzzy) they just changed the tolerance - 230V is +10%/-6% so between 216 and 253V.

Yup 230Vac +/-10% IIRC. I’ve measured 248Vac. That’s not including any transients or harmonics.

Incidentally I’ve also had a good 243Vac in the north of france.

For a 220Vac tube radio, that needed a step down to reduce the unregulated heater supply when used with 243+V mains..
 
This endangers devices who rectify directly from mains with 385V first lytic. In Argentina we use 220V (tolerance from 0 to 230V 😳 🙄). During several years the brand Philco sold CRT color TV with such a values and few years latter the cap exploded just under the CRT neck destroying them. I personally saw those TV's.
 
I'm right at the top level for voltage. Nothing has blown up because of it, but I have to remember when building stuff to remember to allow for it. My oldest power amplifier is a radford STA-25 and that has a number of primary windings to allow for voltage variances, a feature that has gone out of fashion since the 60s.
 
So the 240v can fluctuate anything from 240v up to 253/4v.
Although it 'might' be the case that some devices can handle the higher voltage but what happens to those devices that can't.... shortened life?
European devices are sold for 220/230v....... and many of these devices are sold in the U.K.
As said 230V (+-10 %) in EU is 207-253 V, so the equipment sold in EU should handle this voltages.
 
That's just my thought about the primary winding of the mains Tx.
Should i stick to a 240V input or use the 10% tap being 250v?

It's for a Valve amp i'm building - Tubelab SPP

If the mains input is 240V then you would expect 'X' on the output.
But if it's pushed to 250V then the secondary will also give a slightly higher voltage and i don't want to supply the heaters with a higher +ve
 
Thanks everyone.
Back to the U.K. please.
So it appears the U.K., not being in the EU haven't actually lowered the mains supply to 230V?

If it had been lowered to 230v with a tolerance of +10% -6% then we could have a variable from 216.2 up to 253v.

Instead its still 240v +/- the tolerances.....???
 
Last edited:
AreaRangeLower limit VrmsNominal VrmsUpper limit Vrms
Old UK 240V (1988)+/-6%226240254
Example 220V+/-6% (example)207220233
New EU+/-10%207230253

The new harmonised limits allowed every country to keep their wall voltages basically the same.