I have this big resistive load that I would like to power with about 76v AC. But I figure that would be about 12.16 A and I don't have a transformer like that. But I do have a 44v 16A transformer. So if I simply wire that as a buck transformer I can get my line voltage down to about 76v but my question is how many amps would I now be pulling from the ac outlet ?
The power can only end up in the load (and as losses), so power out = power in - 10% loss.
You can also do the detailed calculation seeing about 4.5A in the primary subtracted from the 12.2A load current...
Get the phasing wrong and you'll see 164V out and > 4kW, so don't get it wrong!
You can also do the detailed calculation seeing about 4.5A in the primary subtracted from the 12.2A load current...
Get the phasing wrong and you'll see 164V out and > 4kW, so don't get it wrong!