I have a pair of Stancor Isolation Transformers connected in series as below:

Isolation #1 Isolation #2
------) (------ ------) (------
) ( ) (
) ( ) (
------) (------ ------) (------
230 120 120 230


1. If I connect the ground only between #1 and #2 would I risk electrocution?
2. If I tie the ground across TAPs, would I negate the benefits of isolation?
3. If I connect it in parallel, would this be equivalent to balanced transformer as discussed elsewhere in the forum?
4. Currently the transformer is causing trips quite frequently, how can I reduce this problem?

Thank you all for your informed advise.
  Reply With Quote
Old 3rd April 2011, 01:36 PM   #2
pirastro is offline pirastro  Singapore
diyAudio Member
 
Join Date: Aug 2009
reposting diagram

Isolation #1 Isolation #2
------) (------ ------) (------
) ( ) (
) ( ) (
------) (------ ------) (------
230 120 120 230
  Reply With Quote
Old 6th April 2011, 04:08 PM   #3
pirastro is offline pirastro  Singapore
diyAudio Member
 
Join Date: Aug 2009
Reattaching as image file thanks.

Click the image to open in full size.
  Reply With Quote
Old 6th April 2011, 04:37 PM   #4
sofaspud is offline sofaspud  United States
diyAudio Member
 
sofaspud's Avatar
 
Join Date: Nov 2005
Location: San Antonio
You have a 2-wire input and a 2-wire output. The 2 are hot and neutral.
I don't know what you mean by "the ground".
  Reply With Quote
Old 6th April 2011, 06:09 PM   #5
zigzagflux is offline zigzagflux  United States
diyAudio Member
 
zigzagflux's Avatar
 
Join Date: Oct 2006
Location: Charlotte, NC
I would ground one of the 120V leads between the transformers. Effectively acts as a shield between first primary and last secondary.

I am not familiar with code requirements in Singapore, but they will govern what you are supposed to do with the 230V secondary with regards to grounding. I would strongly support either grounding one lead (now becomes the neutral) or grounding the center tap (which you do not show as being available).

Floating systems in general are not friendly, and should be avoided unless you plan on performing open heart surgery..
  Reply With Quote
Old 7th April 2011, 01:43 AM   #6
metalsculptor is offline metalsculptor  Australia
diyAudio Member
 
Join Date: Sep 2010
Location: Melbourne
There is no need to ground any of the outputs from the isolation transformer but the amplifier case and any exposed metal must be connected to the power outlet earth and ultimately to the building earth, I am assuming that the code in Singapore is similar to Australia most commonwealth countries derived their electrical code from the UK

AFAIR only extra low voltage equipment is exempt from the case earth requirement. I doubt that an isolation transformer would make the equipment fall under the double insulated earth exemption.
  Reply With Quote
Old 7th April 2011, 02:30 AM   #7
Ruwe is offline Ruwe  Europe
diyAudio Member
 
Join Date: Aug 2008
Location: Vancouver, Canada
I second zigzagflux and would ground one of the 120V lines.

I have an isolation transformer in my audio system and it works better if the secondary is referred to ground ... much more quiet at startup.
In floating mode you'll notice that the voltages between the two lines, with reference to ground, are quite different. In my case I had 40VAC and 80VAC, respectively. I am not sure if that is of any significance to the connected end devices down the line, but at least it's not pleasing to the eye.
  Reply With Quote
Old 7th April 2011, 10:27 AM   #8
AndrewT is offline AndrewT  Scotland
R.I.P.
 
Join Date: Jul 2004
Location: Scottish Borders
a 230:120Vac feeding a 120:230Vac will not give 230Vac.

You need to look at turns ratio for the two transformers.

You can measure turns ratio fairly closely by measuring the open circuit secondary voltage.

Then take account of the voltage drops through the four windings.

If either of the transformers has a dual primary then use the dual primary as the isolated output. The centre tap of the dual primary goes to PE. This gives you an isolated ~110Vac from each of the two output windings. ~220Vac from the out of phase windings.
__________________
regards Andrew T.

Last edited by AndrewT; 7th April 2011 at 10:32 AM.
  Reply With Quote
Old 9th April 2011, 07:08 AM   #9
pirastro is offline pirastro  Singapore
diyAudio Member
 
Join Date: Aug 2009
Thank you all for your advise, the transformer actually has 3 wires, I managed to obtain the the actual schematic from Stancor:

Click the image to open in full size.

I traced the lead in and lead out ground are completely isolated. If I short the ground between the transformer pair it would still be floating. I am concern on the proper connection and safety aspect of the connection.

Since I have two pairs, what are the modes of connection for the ground? Should I short all the 4 grounds then?

I noticed there is a SH sign on the schematic, does it signify the shield is connected to the primary ground? Should I connect the secondary to earth separately

There seem to be two school of thought here
1. to ground at the transformer
2. common ground at amp

What are the pro and cons of each? Thanks
  Reply With Quote
Old 9th April 2011, 05:24 PM   #10
zigzagflux is offline zigzagflux  United States
diyAudio Member
 
zigzagflux's Avatar
 
Join Date: Oct 2006
Location: Charlotte, NC
Assuming you will be connecting 3-1 and 4-2 in the middle of the drawing, and your statement that you are concerned about safety, then I recommend:

Tying all grounds together. It looks like the shield is already bonded to ground, but if not it should be.

Grounding 4-2 in the middle of your drawing.

Bonding 4 (far right of the drawing) to ground. Don't be surprised to hear many suggestions to leave the final secondary isolated. Besides the fact that code does not permit this (at least in the US), there is no demonstrable benefit to leaving the winding floating. On the contrary, there are documented IEEE standards that detail the problems with ungrounded systems.

You will have no ground loops with this method, and will have fantastic common mode filtering of RF and noise in your power supply. If you wanted to reduce differential noise, you could add a X capacitor across the middle 120VAC lines.
  Reply With Quote

Reply


Isolation transformer connectionHide this!Advertise here!
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Using isolation transformer as a PSU transformer??? Yaho Tubes / Valves 10 27th February 2008 05:16 AM
transformer isolation dmitriy167 Solid State 24 2nd March 2005 04:01 AM
Isolation transformer ccozgo41 Swap Meet 0 11th January 2003 02:38 AM
Isolation Transformer Use??? KevinLee Parts 17 8th January 2003 02:45 AM
Isolation Transformer HarryHaller Solid State 9 5th August 2002 01:30 PM


New To Site? Need Help?

All times are GMT. The time now is 09:10 AM.


Search Engine Optimisation provided by DragonByte SEO (Pro) - vBulletin Mods & Addons Copyright © 2018 DragonByte Technologies Ltd.
Resources saved on this page: MySQL 15.00%
vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2018 DragonByte Technologies Ltd.
Copyright ©1999-2018 diyAudio
Wiki