About the grounding tip, i suppose we have some norm about hot and neutral, never respected. But norm is severe with earths diameter and impedance. my suggestion was not to modify wall outlet, but what you call "Power distribution units" ? Right ?

The outlets on the power distribution units are just an extension of the wall outlet. So I fail to see what sort of distinction that is.

Also, inside the equipment, switching and fusing should be done on the hot lead. You go and flip hot and neutral at the outlet or some power distribution unit and now your switching and fusing is on neutral, not hot.

se
 
Yes, but he wasn't talking about doing it inside the piece of gear. He was talking about doing it at the AC outlet.
se

That is US code, where we ground the neutral. Elsewhere they do have a safety ground but both other wires are hot! So some places it is decent practice. (P.S. do resist testing for the hot with your tongue, spend the money on a meter.)


In general or does that change with primary phase?

Thanks
-Antonio

General case. If you are worried about primary to secondary leakage a foil shield can be used. It works for that when it is connected back to the safety ground. But most modern transformers used for audio do not wind the secondary on top of the primary. They used a split bobbin and wind side by side.
 
Stone the Crows.
When i was in charge to the french "Audio Analyst" Pa system, i was very upset about this ! Verifying or make verify the AC between guitar amps and our mikes before each performance or rehearsal: we had often to add earth wires to the guitar amps enclosures (some had even a button to disconnect the earth !!!!!)

The outlets on the power distribution units are just an extension of the wall outlet. So I fail to see what sort of distinction that is.
Steve, I never advertised to modify the Wall outlet, never. The power distributor can-be considered as part of the audio equipment, don't you think ?
It is just to correct the way your audio equipments deal with transformers leakages, witch, as you will see, is not always good. And you are not obliged to do anything, if you don't want to. Not obliged to use C core transformers, as well.
[edit] about fuse and power switch, they deal with currents, and, as long earth is connected, i don't see any inconvenience to set them on neutral or hot as long isolation is correct in the primary of the power transformer.
 
Last edited:
Disabled Account
Joined 2012
This might seem overly simplified but I'll say it anyway because it is a fact: Gounding issues in the home or apartment (potential differences between grnd) are most of the time due to different ground points...... antenna/catv and power not being grounded to the exact same ground point. This is very common in buildings up to the recent past. Codes have been changed for new buildings but that only leaves a hundred million messed up buildings.

Leakage can be checked to see if the products have been UL approved. Old amps of the past used the worst practices.... even connecting hot to chassis via rfi caps to chassis was a common practice.... evenually, with a lot of such equipment in parallel (stage, studio, some home CI) the total combined leakage running thru ground/shields can be a shock! So, even though a product has UL approval on leakage et al, the total leakage on the neutral/grnd can become worrysome even if there is a lot of "OK" products. But, the new products normally in the home (DVD etc) are double insulated and leakage is in the microAmps for them.

Note: Large stage systems in USA for concerts also use 230V balanced power. The power draw is too high for 120v only system. In CI homes, balanced power is often done now via balanced power transformers.... and it is legal under NEC to do so.

Thx--RNMarsh
 
Last edited:
In 1962, we were safety testing a Fender Bassman amp. I told the head of UL about how Fender amps could shock you, if you played in wet weather. I was told that the 'caps' where the leakage currents come from were small enough not to kill. Of course, I had been shocked on someone else's Fender Amp, when we played outside, once, so I knew that it could be VERY UNCOMFORTABLE, if not dangerous. I didn't win the argument.
 
Last edited:
I never advertised to modify the Wall outlet, never. The power distributor can-be considered as part of the audio equipment, don't you think ?

No, I don't think a power distributor can be considered part of the audio equipment. It is an extension of the AC mains.

It is just to correct the way your audio equipments deal with transformers leakages, witch, as you will see, is not always good. And you are not obliged to do anything, if you don't wan to. Not obliged to use C core transformers, as well.

Yes, but you need to realize that not everyone reading your post lives in Europe.

We have a 220 volt system here with the safety ground tied to the AC distribution transformer's center tap so that the safety ground can be used to return fault currents from either side.

However we only use 220 volts for heavy appliances like electric clothes dryers and such. The rest of our homes are wired for 110 volts which taps off one side of the AC distribution transformer and the center tap. That gives us a hot and a neutral and the safety ground is tied to neutral back at the service panel (the main panel where the power enters the home).

So for safety purposes, it's critical that hot and neutral don't get flipped around.

se
 
diyAudio Member RIP
Joined 2005
I probably related the story of a three-piece Harman powered speaker which had a two-wire polarized mains cord. By design the internal transformer primary floated with respect to anything else except hot and neutral, and hot was switched.

A complaint came in that was passed to me that the product was a safety hazard and defective, and a stop ship to Microsoft was advised. My boss said something to the effect that he'd seen things like this before, and it would turn out to be someone who'd modified the unit improperly and was now trying to cover his tracks, and not to worry. He had requested the unit be shipped back for analysis.

I finally saw the emails. The discoverer of the supposed defect was one other than Keith O. Johnson! I advised my boss that this was someone to be taken very seriously indeed.

As best we could reconstruct it, and after conversation with KOJ, it seemed that his particular sample had somehow managed to sustain a short circuit between a.c. neutral and the system common! AFAIK this was a singular event, and the best that could be conjectured was that a bracket had been misinstalled, and instead of being retained by the plastic housing had gotten wedged into a place that accomplished the errant short. Unfortunately in disassembling the unit Keith had destroyed the evidence, and had wound up concluding that the neutral-common connection was intentional!! Of course in virtually any installation, but especially those with a safety-ground-referenced signal source (e.g. a computer sound card) this would at the very least occasion huge amounts of hum and noise.

But for those installations somehow with hot and neutral reversed, it could be catastrophic. And in Keith's case he had his Pacific Microsonics DAC as a source, and was using balanced power (was it Equitech?) for mains. So hot and neutral had ~60VAC on each relative to safety ground. The speaker promptly blew out the DAC. Ouch.

I was able to persuade him that in no way was this issue related to the design, other than in terms of failing to anticipate the possibility of misassembly. We instituted a test on the production line for verifying high resistance between mains in and signal common. But as far as I know this was a singular defect, yet one that found its way into the hands of a singular person!
 
Disabled Account
Joined 2012
This might seem overly simplified but I'll say it anyway because it is a fact: Gounding issues in the home or apartment (potential differences between grnd) are most of the time due to different ground points...... antenna/catv and power not being grounded to the exact same ground point. This is very common in buildings up to the recent past. Codes have been changed for new buildings but that only leaves a hundred million messed up buildings.

Leakage can be checked to see if the products have been UL approved. Old amps of the past used the worst practices.... even connecting hot to chassis via rfi caps to chassis was a common practice.... evenually, with a lot of such equipment in parallel (stage, studio, some home CI) the total combined leakage running thru ground/shields can be a shock! So, even though a product has UL approval on leakage et al, the total leakage on the neutral/grnd can become worrysome even if there is a lot of "OK" products. But, the new products normally in the home (DVD etc) are double insulated and leakage is in the microAmps for them.

Note: Large stage systems in USA for concerts also use 230V balanced power. The power draw is too high for 120v only system. In CI homes, balanced power is often done now via balanced power transformers.... and it is legal under NEC to do so.

Thx--RNMarsh
 
So for safety purposes, it's critical that hot and neutral don't get flipped around.
No. For safety purpose, it is critical the parts of your equipment witch can be touched with your body are connected to the main earth/ground. And your differential protection (Safety disconnect switch) effective.
But for those installations somehow with hot and neutral reversed, it could be catastrophic.
In a way, if there is a short circuit between one of the plug wires and the earth, i prefer if it is between the hot and the earth inside a device. The safety switch will switch off as soon as the device will be plugged, warning-you of the defect. it works most of the time with the neutral too, but not with so much margin.
A lot of controversy about a simple tip to get a better sound because less noises in the signal cables. A little too much, don't you think ?
About power switches inside your equipment, i hope the manufacturer was clever enough to cut the two AC lines before the transformer. In EU, it is a legal requisite.
If not, you will have added noise, even if this equipment is powered off.
 
Last edited:
No. For safety purpose, it is critical the parts of your equipment witch can be touched with your body are connected to the main earth/ground. And your differential protection (Safety disconnect switch) effective.
In a way, if there is a short circuit between one of the plug wires and the earth, i prefer if it is between the hot and the earth inside a device. The safety switch will switch off as soon as the device will be plugged, warning-you of the defect.

Hate to inform you, but most homes in the US are not wired with GFCI's.

I'm done here.

*sigh*

se
 
GFCI is in all of our bathrooms but these are individual units, not whole house systems. It will only shut down the local outlet. It should be whole house but some day that will happen. Not a bad idea in the kitchen also as anywhere you could have water. This is where we get in trouble when we talk generalities, so much different between our power delivery systems. Don't I remember that there are still some power plants with 50hz power on the East Coast?
 
Hate to inform you, but most homes in the US are not wired with GFCI's.
Oh! I could not imagine that, sorry. Is-it because you run only 110V that your country take less precautions than us ? In France, all the power plugs are equipped with an earth plug, and there is GFCI ('differential') in the central board for each room plus one main for the house/apartment.

I use for my electronic equipment (including TV and computer) power distribution units equiped both with a GFCI and a ultra fast protection against over-voltages, like the ones witch can be induced by lightning. It saved my equipment several time, during stormy days.
As i was bored with the noise induced by my computer, i changed my connections between it and my audio system for optical digital and opto isolated RS132, in order to have ground isolation between them. The change in sound transparency was noticeable.

Well, i have read the Bruno's white paper about power 1 bit converter (no amplifier, no feedback). We will be rid of all those analog problems soon ?
 
Hey Esperado,

Yes, in Canada as well you don't want to switch hot/neutral and GFCIs are relatively new and usually restricted to plugs within ~1.5 m of a water source (bathroom sink, kitchen, laundry, ...).

I have a GFCI in the basement that was up to electrical code a few years ago and now doesn't meet it (and some unaware/ unscrupulous retailers continue to sell the old ones with little info ...). :(

The computer I'm on is connected by low WAF extension cord to another room because ... this room has non-keyed hot/neutral and the ground plug is connected to ... nothing!?! :eek:

Another plug had hot/neutral reversed and there are 4 plugs in the basement that have gnd but ... nothing else? WTF!?! And don't even get me started on the light fixtures, plumbing and eaves-through! And this was after a "safety" inspection! Grrrr, Ah, now I'm all pissed!

Yes, we're Neanderthals over here and we deserve a good zapping!

However, because this is the Interwebs connecting distant lands and because there are people dumb enough to "try something they heard on the ...", you might want to include something like:

***!!***Caution, don't open it if you don't know what you're doing***!!***
***!!***Consult your local electrical safety regulations***!!***
***!!***Yes, you dumbass because you would actually try it!***!!***

:up:

Cheers,
Jeff
 
Last edited:
...
The other issue is the use of Belden 1023A cable. It is a shielded twisted pair with a foil shield. HOWEVER one conductor is copper the other is constantan! It is intended to attach to thermocouple and not introduce any voltage errors.

And just to show how strange the human brain is:

Constantan, attach thermocouple
Constantan, attach thermocouple
Constantan, attach thermocouple
Constantan, thermo thermocouple!


50 Quatloos to the namer of the reference!

P.S. Oh, you're gonna hate me! Once that's in your head ... tee hee ...
 
Last edited:
diyAudio Member RIP
Joined 2005
And just to show how strange the human brain is:

Constantan, attach thermocouple
Constantan, attach thermocouple
Constantan, attach thermocouple
Constantan, thermo thermocouple!


50 Quatloos to the namer of the reference!

P.S. Oh, you're gonna hate me! Once that's in your head ... tee hee ...
It has a distant reference to another similarly-syncopated tune, Putting on the Litz
 
Member
Joined 2002
Paid Member
I'm done here.
se



Steve, don’t get upset :)

In many European countries the AC domestic receptacle/plug is by code of the Schuko type.
Schuko - Wikipedia, the free encyclopedia

With these, live and neutral can be on either pin at the consuming device. (Earth prong also is the first to engage and the last to disengage)

Distribution transformers on the utility network are not of the balance type with a center tap. They are 3 phase, either delta or star, so any phase is symmetrical to the single common neutral (return) line. Phase to neutral=230V/50Hz

Differential GFCI is mandatory (at least one on each distribution panel).