Rail voltage compared to transformer voltage

Status
This old topic is closed. If you want to reopen this topic, contact a moderator using the "Report Post" button.
Account Disabled
Joined 2002
I will be using a 13.5 volt transformer with a 20 amp capacity. I will draw approx. 6 amps current DC- 60000µF filtering, capacitive input. Can someone tell me what I should expect my rail voltages to be? I thought it would be theoretically 1.4 times the 13.5= approx. 18.9V. I read in the pass labs A75 article that the transformer will load down, so that it will be about 1.2 times the 13.5= 16.2V. Is there any way to predict?
Steve
 
sam9

Having bought a transformer or two, I can appreciate the problem. Some like Avel-Lindberg include a state called " regulation", expressed in percent. For instance, if you buy a 13.5V transformer with 6% regulation from them and measure the secondary voltage without a load it will be 13.5V x 1.06 =14.3V. This accounts for what they expect the drop under load to be. On top of that, manufactures want those specs to always be met so they tend to de-rate them a little, maybe another 5%. Transforners I've bought from Plitron and Avel-Lindberg both were this way.

This sounds nice unless you are in a situation where you have an upper limit on the rail voltage due to possible damage to components. I ran into this once and had to do a quickie fix by adding a pair of + & - voltage regulators to what should have been an unregulated supply. Eventually, I replaced the transformer.

So anyway here is the modified calculation I apply to the spec sheets:

(Stated Voltage) x 1.1414 x (1+stated "regulation" %) x (1.05 for under-rating).

Example (13.5V x 1.1414 x 1.06 x 1.05)-1 = 16.1V expected unloaded reading at the rsulting rails . The "-1" is what I expect a 25 amp bridge rectifier to drop, other rectification methods my differ.
 