Old 11th October 2004, 03:31 AM   #1
lopan is offline lopan  United States
diyAudio Member
 
Join Date: Sep 2004
Location: California
Default three prong receptacle with 50 volts on ground

I am not sure which forum to put this on but you guys are power buffs so I will start here. In checking the polarity of my wall receptacles I found one where the ground was 50+ volts above neutral and 60+ volts below hot. So I replaced it with a new high grade recptacle -- same thing. There is no ground wire or metal conduit and therefore no actual grounding. But jI don't understand why there is a 50 volt potential sitting on this ground.

Can any one explain this?

Thanks
  Reply With Quote
Old 11th October 2004, 04:58 AM   #2
djk is offline djk
diyAudio Member
 
djk's Avatar
 
Join Date: Feb 2001
Location: USA
Something in the house is plugged in that has some leakage.

As a test, hook a 100W lightbulb from neutral to gnd.

I bet all the voltage goes away.

If it doesn't, then leave the lightbulb and the meter hooked up and throw the breakers one at a time until you isolate the circuit. Then unhook each item on that circuit one at a time until you find it.

A GFI takes several mA to trip, a digital meter with a 10,000,000 ohm input impedance will read voltage with a few A of current.
  Reply With Quote
Old 11th October 2004, 05:05 AM   #3
lopan is offline lopan  United States
diyAudio Member
 
Join Date: Sep 2004
Location: California
Default thanks

good idea I will try this


I try with a 10 ohm resistor and it did go away -- now I will try to isolate as you outlined

take care
  Reply With Quote
Old 11th October 2004, 05:42 AM   #4
diyAudio Member
 
Join Date: Apr 2001
Location: Santa Cruz, CA
Default Other things to consider....

You didn't say how old your house wiring is but I've run into problems with corrosion where any wire joints are made - especially if you're close to salt water, there have been additions to the house, or if you've had other weird problems such as breakers tripping at odd times.

The trick to working through electrical gremlins like you've described is a clear process of deduction. I'd suggest you take notes as you determine what it is not first.

Hope that helps.

Cheers,

David
  Reply With Quote
Old 11th October 2004, 06:09 AM   #5
lopan is offline lopan  United States
diyAudio Member
 
Join Date: Sep 2004
Location: California
Default I think I was unclear

There is NOTHING connected to the ground screw of the recepticle just the hot and the neutral. Yet when I measre the voltage from the ground pin to the neutral or hot there is a 50 to 60 volt differential. Like leakage in the receptacle.

My house is 30 years old. I ran all new circuits for my amps 2 30 amp grounded circuits and was using this 20 amp circuit for the microelectronics. But I had a small buzz in the tweeters and was trying to find it. Once I connected everyting to an extension cord from a truely grounded receptacle the buz was gone.

Thanks
  Reply With Quote
Old 11th October 2004, 06:10 AM   #6
djk is offline djk
diyAudio Member
 
djk's Avatar
 
Join Date: Feb 2001
Location: USA
"I try with a 10 ohm resistor and it did go away -- now I will try to isolate as you outlined"

If the digital meter is the only load, the leakage resistance in your circuit is on the order of 1,000,000 ohms or higher, that was why the lightbulb was suggested.

Measure the current through the lightbulb, if it is less that 10mA don't even worry about it (10mA would be a 12K leakage resistance).

A lightbulb is preferred for testing as it will not blow up in your face (like a small resistor) if there is a fault.
  Reply With Quote
Old 11th October 2004, 06:21 AM   #7
lopan is offline lopan  United States
diyAudio Member
 
Join Date: Sep 2004
Location: California
Default thanks again

-
  Reply With Quote
Old 11th October 2004, 01:36 PM   #8
diyAudio Member
 
jneutron's Avatar
 
Join Date: Jan 2004
Location: away
Default Re: I think I was unclear

Quote:
Originally posted by lopan
There is NOTHING connected to the ground screw of the recepticle just the hot and the neutral. Yet when I measre the voltage from the ground pin to the neutral or hot there is a 50 to 60 volt differential. Like leakage in the receptacle.

My house is 30 years old. I ran all new circuits for my amps 2 30 amp grounded circuits and was using this 20 amp circuit for the microelectronics. But I had a small buzz in the tweeters and was trying to find it. Once I connected everyting to an extension cord from a truely grounded receptacle the buz was gone.

Thanks
If the recepticle ground is not connected, then you are reading halfway between neutral and hot. What you are looking at is a divider between those two..it is probably some combination of resistance/capacitance. If it is resistance, you may be able to lessen the effect by putting in a new recepticle..if it is capacitance, it won't be fixed that way. But the input impedance of your voltmeter doesn't load the divider down, giving you the readings. And that resistor? What if it had been a hard 50 volts?? Did you have safety goggles on when you did this, or did you use a 250 watt resistor to be safe?

I had to troubleshoot a circa 1900 house coupla months ago, and the 75 volts on neutral at a chandelier was VERY hard..it was the 240 volt system of the house that was hugely imbalanced, with very bad mains grounding..so I think providing this advice is good..

The GFI idea is a very good one. But, be aware that the self test feature of the GFI (that red button) requires the ground to function properly, you will not be able to test the GFI unless you wire a proper ground..and I recommend testing any GFI every week or so.

Cheers, John
  Reply With Quote
Old 12th October 2004, 06:02 AM   #9
diyAudio Member
 
kilowattski's Avatar
 
Join Date: Aug 2003
Location: Long Island, New York
The code says that neutral and ground are to be tied together back at the box and every outlet should be grounded. It sounds as if there is some resistance between the two between the box, and the outlet. If you wired these new circuits, it sounds as if you don't have a clue to what you are doing, and if I were you, I would get an electrician pronto, because this is dangerous and should be rectified immediately.
__________________
-----------------------------------------------
Kilowattski
  Reply With Quote
Old 12th October 2004, 07:22 AM   #10
lopan is offline lopan  United States
diyAudio Member
 
Join Date: Sep 2004
Location: California
Default yeah brainchild

read the post before you respond and know what your talking about before you respond and think before you speak
  Reply With Quote

Reply


Hide this!Advertise here!
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
3 prong speaker Bob0513 Multi-Way 15 8th March 2008 01:34 AM
power transformers 220 volts to 110 volts garydmd Chip Amps 3 7th April 2007 02:52 PM
Gainclone is on 120 volts will it be fine at 220 volts? Jimmy154 Chip Amps 7 29th June 2005 12:10 AM
2 To 3 Prong Conversion amaturetuber Tubes / Valves 3 8th May 2005 10:20 AM
does connecting mains ground with circuit ground create a ground loop? jarthel Everything Else 0 25th June 2003 12:55 PM


New To Site? Need Help?

All times are GMT. The time now is 01:37 AM.


vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.
Copyright 1999-2014 diyAudio

Content Relevant URLs by vBSEO 3.3.2