Default secondary in parallel/series with primary

What are the risks involved if I hook up a secondary in series with primary to theoretically increase primary windings to reduce output voltage?

vs.

What are the risks involved in hooking up the secondary in parallel and out of phase with primarys to reduce output voltage?
  Reply With Quote
Old 11th August 2012, 03:32 PM   #2
AJT is offline AJT  Philippines
diyAudio Moderator
 
AJT's Avatar
 
Join Date: May 2003
Location: Palatiw, Pasig City
such pratice is not encouraged here unless you are using isolation transformers, electricution hazards are real.......
__________________
the best advertisement for a good audio design is the number of diy'ers wanting to build it after all the years....never the say so of so called gurus....
  Reply With Quote
Old 11th August 2012, 07:16 PM   #3
DF96 is offline DF96  England
diyAudio Member
 
Join Date: May 2007
Secondaries should only be connected in series with the primary, and only if those secondaries are not required for any other purpose and if they have sufficient insulation for mains potential. I would recommend attaching a label to the transformer to warn unsuspecting people that this has been done. In a few years time you may have forgotten what you did.

Never connect two windings in parallel (primary or secondary) except when they are identical.
  Reply With Quote
Old 11th August 2012, 08:02 PM   #4
Elvee is offline Elvee  Belgium
diyAudio Member
 
Elvee's Avatar
 
Join Date: Sep 2006
Quote:
Originally Posted by DF96 View Post
Secondaries should only be connected in series with the primary, and only if those secondaries are not required for any other purpose and if they have sufficient insulation for mains potential.
It is not generally the case: the mains safety isolation barrier is between the primaries and all secondaries.
The secondaries themselves often rely on the wire enamel for sole isolation material.
There are exceptions: transformers for oscilloscopes, variable frequency drives, etc, but no basic general purpose transformer is built like that.
__________________
. .Circlophone your life !!!! . .
♫♪ My little cheap Circlophone© ♫♪
  Reply With Quote
Old 11th August 2012, 08:29 PM   #5
DF96 is offline DF96  England
diyAudio Member
 
Join Date: May 2007
Yes, I suspected that might be the case so the answer to the OP's question is No - unless you are absolutely sure your transformer is suitable.
  Reply With Quote
Old 12th August 2012, 12:02 AM   #6
diyAudio Member
 
Join Date: Apr 2008
So, the secondary is to only be hooked up in series if this is to be done.

The transformer is in a housing and sealed in an epoxy like substance (I assume to reduce vibration). When hooked up properly to 120V the (unused) secondary has 20V across it. I'm unable to see the actual wire that's wraped around the core, but the lead comming from it is rated for 300V, I don't trust that to be the rating of the secondary.

Is there another way to tell what the secondary's voltage rating is?

Last edited by scutterflux; 12th August 2012 at 12:04 AM.
  Reply With Quote
Old 12th August 2012, 01:05 AM   #7
AJT is offline AJT  Philippines
diyAudio Moderator
 
AJT's Avatar
 
Join Date: May 2003
Location: Palatiw, Pasig City
use a dmm set to voltage to measure it....


a picture of your traffo can help....
__________________
the best advertisement for a good audio design is the number of diy'ers wanting to build it after all the years....never the say so of so called gurus....
  Reply With Quote
Old 12th August 2012, 03:52 AM   #8
diyAudio Member
 
zigzagflux's Avatar
 
Join Date: Oct 2006
Location: Charlotte, NC
I do it all the time, works great when you have unused windings (especially that 5V winding intended for a tube rectifier). When you need to bring that voltage down just a little.

Best bet is to connect the secondary winding at the neutral end of the circuit, but ultimately I don't think there are extreme insulation concerns. If you were using the 5V winding (just as example) on a directly heated rectifier, no one panics about the insulation rating.

Keep in mind if your transformer is equipped with an electrostatic shield, using a secondary winding in the primary essentially negates the action of the shield.
  Reply With Quote
Old 12th August 2012, 12:21 PM   #9
diyAudio Member
 
darkfenriz's Avatar
 
Join Date: Jun 2004
Location: Warsaw
Quote:
Originally Posted by Elvee View Post
It is not generally the case: the mains safety isolation barrier is between the primaries and all secondaries.
The secondaries themselves often rely on the wire enamel for sole isolation material.
There are exceptions: transformers for oscilloscopes, variable frequency drives, etc, but no basic general purpose transformer is built like that.
Yes, and that's why it is potentially lethal and definitely illegal. Unless you are absolutely sure it is not.
  Reply With Quote
Old 12th August 2012, 04:43 PM   #10
DF96 is offline DF96  England
diyAudio Member
 
Join Date: May 2007
Quote:
Originally Posted by Tony
use a dmm set to voltage to measure it...
Most DMM measure voltage. I have never seen one which measures the voltage rating of insulation. For that you need something like a Megger.

Quote:
Originally Posted by zigzgflux
If you were using the 5V winding (just as example) on a directly heated rectifier, no one panics about the insulation rating.
That winding will have been built for high voltage operaton, because the transformer designer will know that a 5V heater winding is intended for a rectifier. Not all secondaries are.
  Reply With Quote

Reply


Hide this!Advertise here!
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
is transformer with primary and secondary = isolation? milen007 Power Supplies 5 1st February 2011 12:30 PM
Using primary as the secondary winding in the power transformer. mishak Parts 10 30th May 2010 06:55 AM
safest way to identify primary/secondary? gary h Power Supplies 15 6th January 2010 04:56 PM
cap btween primary and secondary windings? sam9 Power Supplies 8 19th May 2005 07:34 PM
Why a Zobel network across OPT primary or secondary? ray_moth Tubes / Valves 6 4th March 2005 11:26 PM


New To Site? Need Help?

All times are GMT. The time now is 06:25 AM.


vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.
Copyright ©1999-2014 diyAudio

Content Relevant URLs by vBSEO 3.3.2