I scrounged a 900VA+ transformer from an old battery backup and I can't find any information on it. I have plugged it in and it trips a 120V 20A breaker every time. I am wondering about using NTC Thermistors to limit my inrush current. Would it just be easier to build a soft start circuit?
  Reply With Quote
Old 25th March 2011, 06:35 PM   #2
ywara is offline ywara  United States
diyAudio Member
 
Join Date: Mar 2011
I'd say that ICLs are probably easiest, though the on resistance could possibly be a problem if you don't have any headroom.
  Reply With Quote
Old 25th March 2011, 07:13 PM   #3
AndrewT is offline AndrewT  Scotland
diyAudio Member
 
Join Date: Jul 2004
Location: Scottish Borders
The recommended fuse rating for a motor and for a transformer is
3times the power divided by the supply voltage.

Your 900VA running on 115Vac would require approximately >=23.5A fuse to start up reliably.
You may find that you have to use a B or C rated 25A breaker to get it to start up.

Alternatively fit a soft start using either suitably rated Power Thermistors or Power Resistors.
__________________
regards Andrew T.
  Reply With Quote
Old 25th March 2011, 07:16 PM   #4
Einric is offline Einric  United States
diyAudio Member
 
Einric's Avatar
 
Join Date: Feb 2011
Location: Bozeman, MT
I figured on using power thermistors. My breaker is a 20A Class C. It would make sense that I would trip the breaker if I was trying to pull almost 24A across it.
  Reply With Quote
Old 25th March 2011, 07:35 PM   #5
Electrons are yellow and more is better!
diyAudio Member
 
peranders's Avatar
 
Join Date: Apr 2002
Location: Göteborg, Sweden
Blog Entries: 4
Quote:
Originally Posted by Einric View Post
Would it just be easier to build a soft start circuit?
Probably. Have you noticed my group buy?
__________________
/Per-Anders (my first name) or P-A as my friends call me
  Reply With Quote
Old 25th March 2011, 07:36 PM   #6
Einric is offline Einric  United States
diyAudio Member
 
Einric's Avatar
 
Join Date: Feb 2011
Location: Bozeman, MT
No I have not.
  Reply With Quote
Old 25th March 2011, 09:47 PM   #7
AndrewT is offline AndrewT  Scotland
diyAudio Member
 
Join Date: Jul 2004
Location: Scottish Borders
Hi,
the transformer will be pulling a lot higher than 24Apk at start up.
Have a look at the time vs current of a ClassC breaker.
The transient that can pass for short periods is many times the rated breaker value.

At some point in the starting sequence your transformer is taking the breaker outside the ClassC curve. It might be at the very first instant of 1us after closing the switch , or it might be after 1ms after closing the switch.
More likely it is an accumulation of [i^2t] that opens the breaker.

The same happens with a fuse.
What you try to do is keep the current during the first few millisecond under some form of control so that the transient current limits for the chosen breaker an/or chosen fuse are not exceeded.
Soft start is designed to specifically control the starting currents.
__________________
regards Andrew T.
  Reply With Quote
Old 26th March 2011, 01:49 PM   #8
diyAudio Member
 
Join Date: Sep 2010
Location: Melbourne
Quote:
Originally Posted by Einric View Post
I scrounged a 900VA+ transformer from an old battery backup and I can't find any information on it. I have plugged it in and it trips a 120V 20A breaker every time. I am wondering about using NTC Thermistors to limit my inrush current. Would it just be easier to build a soft start circuit?
It is strange that it trips every time, check there is not some other issue, Random trips are more characteristic of inrush current. 900VA is not a large transformer, 2 Kva transformers do not cause inrush current trips on the 240V domestic supply over here. (C curve breakers)
  Reply With Quote
Old 26th March 2011, 03:01 PM   #9
diyAudio Member
 
BobEllis's Avatar
 
Join Date: Sep 2003
Location: Upstate NY
light bulb tester time. Use a 40-60W light bulb in series with the transformer. If the bulb stays on after the initial surge there is an issue with the transformer.
  Reply With Quote
Old 26th March 2011, 04:52 PM   #10
Einric is offline Einric  United States
diyAudio Member
 
Einric's Avatar
 
Join Date: Feb 2011
Location: Bozeman, MT
I'll have to look into building a light bulb tester.
  Reply With Quote

Reply


Hide this!Advertise here!
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inrush limiting circuit pona Parts 1 16th October 2010 10:32 AM
Inrush current limiting heater filaments boywonder Tubes / Valves 14 2nd February 2009 08:33 AM
Inrush current limiting necessary for EI transformers Bama Slamma Power Supplies 10 6th November 2006 06:08 PM
Limiting Inrush?? Deltat Power Supplies 11 31st March 2006 04:38 PM
Inrush Current Limiting Circuit haldor Parts 22 8th October 2004 04:06 PM


New To Site? Need Help?

All times are GMT. The time now is 10:09 PM.


vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.
Copyright ©1999-2014 diyAudio

Content Relevant URLs by vBSEO 3.3.2