Just wondering, since transformer VA rating roughly correlates to weight, would a given autoformer VA rating roughly match twice the VA rating of an equal weight transformer? Or some other ratio such as 1:1?
If you're wanting background, this is because I'm trying to very roughly gauge the rating of some surplus 120/240 autoformers.
__________________
Aerodynamics are for people who can't build engines. Enzo Ferrari |
|
|
|
|
#2 |
|
diyAudio Member
Join Date: Jul 2004
Location: Scottish Borders
|
basically it's a current rating, determined by the wire used for the windings.
If you use a 240Vac transformer that is tapped at 120Vac and the whole winding is 3Aac rated then the most you can take from it is always 3Aac. Much more likely is that the windings use different wire diameters/areas and you must then ensure you use the autoformer the right way round to get the extra current capacity of the thicker winding. If the voltage tapping is very low eg 230/240 volt (10V tapping) then the whole transformer can supply ~10times the power of the main winding IF THE 10V tapping has SUFFICIENT copper area.
__________________
regards Andrew T. |
|
|
|
|
#3 |
|
diyAudio Member
Join Date: Jan 2003
Location: Solna
|
A 2:1 (for example 240/120V) autotransformer does have double the power rating of what an isolating transformer on the same core would have had. Different ratios give different results, however.
__________________
The bewitching snivvie is dulcet paragon. |
|
|
|
|
#4 |
|
diyAudio Member
|
Hi,
according to the Radiotron Designer's Handbook, chapter 5 on page 235, VA equals the square of the product of core area in square inches times a constant 5.58.... so if you know the center leg and stacking height of your traffo, you can compute for the VA rating.
__________________
http://www.electronicslab.ph/forum/i...?topic=32688.0 |
|
|
|
|
#5 |
|
diyAudio Member
|
hi, auto transformers have both conduction and induction at their outputs so they are definitely smaller than isolated winding ones for the same VA rating
__________________
http://www.electronicslab.ph/forum/i...?topic=32688.0 |
|
|
|
|
#6 | |||
|
diyAudio Member
Join Date: Sep 2006
|
Quote:
Quote:
Quote:
|
|||
|
|
|
|
#7 | |
|
diyAudio Member
Join Date: Sep 2005
|
Quote:
http://www.plitron.com/technotes.asp Autoformers For applications requiring either a simple step-up or step-down of voltage, and where there is no need for electrical isolation between windings, an autoformer can be used. Significant size and weight reductions can result over isolated transformers. The power rating of an autotformer is given by the expression: VA rated = POUT x (V HI - V LOW) / V HI |
|
|
|
|
|
#8 | |
|
diyAudio Member
Join Date: Jul 2004
Location: Scottish Borders
|
Quote:
I do not agree. The step down auto transformer will have a low voltage tapping that passes the whole output current. This winding must be rated for the desired output current. For 2:1 step down the low voltage winding will have approximately double the wire area to pass double the current. If the output winding is the same area as the whole primary winding then that wastes copper area in the high voltage side. this increases weight and volume and may force the manufacturer to adopt a bigger core just to fit all that copper in. To get the full benefit of the smallness of the auto transformer all the windings must be current rated for the current they are required to pass.
__________________
regards Andrew T. |
|
|
|
|
|
#9 |
|
diyAudio Member
Join Date: Jan 2003
Location: Solna
|
Half the output current flows "down" from input to output while the same amount flows "up" through the "common" part of the winding. This is the point of using an autotransformer. Transformer winding current is thus only half of the output current for a 2:1 autotransformer. If output is 120V 1A (120VA), only 60VA needs to be transferred through the transformer from upper to lower winding.
Code:
2:1 autotransformer example.
0.5A
------>
--------+
|
|| *)
|| ) |
|| ) | 0.5A
|| ) |
|| ) +-> 1A
|| | ---->
|| +-----------¤
|| |
|| *) +->
|| ) |
|| ) | 0.5A
|| ) |
|| )
|
0.5A | 1A
<---- | <-----
--------+------------¤
__________________
The bewitching snivvie is dulcet paragon. Last edited by megajocke; 19th September 2009 at 08:04 PM. |
|
|
|
|
#10 | |
|
diyAudio Member
Join Date: Jul 2004
Location: Scottish Borders
|
Quote:
How can a winding that all goes in the "same" direction pass currents in opposite phase to the output?
__________________
regards Andrew T. |
|
|
|
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
|
|
|
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Transformer rating ? | woody | Parts | 0 | 31st July 2008 05:44 PM |
| Zen transformer rating!! | sandstorm33 | Pass Labs | 13 | 14th December 2007 02:42 PM |
| Using transformer primary as an autoformer | stoolpigeon | Everything Else | 8 | 22nd April 2007 06:17 AM |