Default UK laws - dealing with ground loops?

Hi folks.

Does anyone know if the circuit discribed here is legal to implement in the UK, for a valve poweramp (Dynaco ST70):

http://sound.westhost.com/earthing.htm

I have an earth loop but I don't wish to disconnect any of the safety earths, and this looks like an ideal solution, short of converting all my gear to balanced signal interconnects!

Many thanks,

- John
  Reply With Quote
Old 4th August 2008, 11:52 AM   #2
Mooly is online now Mooly  United Kingdom
diyAudio Moderator
 
Mooly's Avatar
 
Join Date: Sep 2007
Hello again John,
You mean the bridge rectifier I take it, for lifting ground impedances. Is it legal ? I am 99.99999% sure the answer is no, for the reason that the earth connection has to be "direct" and meet absolute requirements for minimum impedance etc in the event of a fault. It would fail on all counts.
The earth connection has to be able to carry the full fault current ie live to earth short until the fuse blows, and to be able to do it repeatedly time after time.
That said in practice it probably would be O.K. If a fault occurred diode bridges usually fail short circuit under overload but IT CANT BE GUARANTEED. Do you see the problem. If it failed open circuit the protection would be removed.
  Reply With Quote
Old 4th August 2008, 11:54 AM   #3
Gordy is offline Gordy  United Kingdom
diyAudio Member
 
Join Date: Nov 2006
As soon as the earth cable enters the unit take it to a good solid ground point on the case (...assuming a metal case of course). If you have a multi-part case make sure each part of the case conducts to that point (...just resistance test it).

The rest is up to you. 'Lifting' the audio ground to break a loop is common practice. The ESP circuit looks comprehensive. Substituting two 1N4007 diodes reverse strapped across each other is usually as good as the bridge though.

If your mains transformer has a steel case remember to ground it to the amplifier case.
  Reply With Quote
Old 4th August 2008, 12:07 PM   #4
Gordy is offline Gordy  United Kingdom
diyAudio Member
 
Join Date: Nov 2006
Quote:
Originally posted by Mooly
Hello again John,
You mean the bridge rectifier I take it, for lifting ground impedances. Is it legal ? I am 99.99999% sure the answer is no, for the reason that the earth connection has to be "direct" and meet absolute requirements for minimum impedance etc in the event of a fault. It would fail on all counts.
The earth connection has to be able to carry the full fault current ie live to earth short until the fuse blows, and to be able to do it repeatedly time after time.
That said in practice it probably would be O.K. If a fault occurred diode bridges usually fail short circuit under overload but IT CANT BE GUARANTEED. Do you see the problem. If it failed open circuit the protection would be removed.
Refering to Figure 3. on the ESP site (http://sound.westhost.com/earthing.htm) then the ground is made to the case immediately upon entry, which is fine. If there is a subsequent fault the worst case scenario is a power short to chassis ground, which would connect directly to the grounded earth point and the fuse / ELCB would trip in the house distribution board.

If there is a more minor fault on the audio circuit board then the resistor will conduct and the ELCB in your home's distribution panel should trip. If the current is so great as to create a 1.4 Volt drop across the resistor then the diodes of the bridge will conduct.

Admittedly it's been lots of years since I looked at the regs, but I think this set-up should be fine.
  Reply With Quote
Old 4th August 2008, 12:11 PM   #5
diyAudio Member
 
Join Date: Jul 2003
Location: Bath, UK
Gordy's right - but just top make this really clear, the problem really rests with the ambiguous way the word 'ground' is used.

If your equipment has conductive cases they must be bonded to the mains Earth to minimise shock*

Tha 0v side of the circuitry within that case does not have to also bonded to mains earth, but in any system it should be, once, for safety. You can control how and where this is done. If you have only one such Earth-0v bond in a system, you have no 'earth loops' by definition, but you must ensure that any interconnects can carry the propsective fault currents and/or fuse the secondary side of circuit supplies to ensure disconnection in the case of a fault to Earth.

The purpose of ESP circuit is in this latter link, to separate the circuit 0v side from the Mains earth, but in a manner that can carry fault current.


* unless 'Double Insulation' standards are adhered to. Without stringent testing this is not a suitable DIY technique
  Reply With Quote
Old 4th August 2008, 12:11 PM   #6
Mooly is online now Mooly  United Kingdom
diyAudio Moderator
 
Mooly's Avatar
 
Join Date: Sep 2007
IN4007 WILL explode under fault conditions. They are 1 amp devices. These were often used as bridge rectifiers in TV's VCR's etc . Seen it countless times. Two bits of wire where once lived a diode.
This is the problem of dubious advice. A huge bridge rectifier may survive or fail at least short so giving continued protection but as said NO GUARANTEES
  Reply With Quote
Old 4th August 2008, 12:51 PM   #7
Gordy is offline Gordy  United Kingdom
diyAudio Member
 
Join Date: Nov 2006
Diodes exploding before circuit breaker trips? Possible I suppose, and no guarantees as you say. In which case 3 spent on a chunky 35 Amp bridge rectifier might be money very well spent.
  Reply With Quote
Old 4th August 2008, 01:47 PM   #8
Did it Himself
diyAudio Member
 
richie00boy's Avatar
 
Join Date: Nov 2003
Location: Gloucestershire, England, UK
Just to add another voice that 1N series diodes would be completely unaccaptable. A creative portable appliance tester might find a way to test the equipment in such a way that the 20A test current is passed through the loop breaker, and if 1A diodes were used for this purpose then I hope it's now blindingly clear what the consequences would be.
__________________
www.readresearch.co.uk my website for UK diy audio people - designs, PCBs, kits and more.
  Reply With Quote
Old 4th August 2008, 03:30 PM   #9
Gordy is offline Gordy  United Kingdom
diyAudio Member
 
Join Date: Nov 2006
As an aside: Portable Appliance Testing is completely irrelevant for your personally owned domestic items, even more so if you have built it yourself !
  Reply With Quote
Old 4th August 2008, 04:05 PM   #10
Did it Himself
diyAudio Member
 
richie00boy's Avatar
 
Join Date: Nov 2003
Location: Gloucestershire, England, UK
So true, but surely it's good practice to build your kit to pass safety standards?
__________________
www.readresearch.co.uk my website for UK diy audio people - designs, PCBs, kits and more.
  Reply With Quote

Reply


Hide this!Advertise here!
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ground loops and containment jneutron Parts 49 18th February 2011 03:28 PM
Ground loops, speaker hum and buz steevo Solid State 15 31st October 2008 10:58 PM
Safety question concerning ground loops derMichi Chip Amps 5 9th June 2006 09:31 AM
P3A and ground loops biff584 Solid State 5 14th March 2003 03:21 PM
Earth/Ground Loops JohnClark Tubes / Valves 2 14th November 2001 01:49 AM