I have bought some very nice Military surplus transformers (steel potted, apparently very high quality) .
primary 115V/0.7A and sek. 6.3V/12A (and with shield) I intended to connect two primary windings in series for 230V line voltage application. So far so good. But one thing I have overlooked - they`re rated for 400Hz line frequency (as most of the Military power stuff) ![]() Is there any way to use them on 50Hz line frequency though? I believe it should be possible but very likely don`t get the rated power out of them. Do You think I can use them on 50Hz at all? If yes, what do You think which amount of decrease in output power I have to expect - 20%- 30% - or even more? Thank You for any kind of input!
__________________
Christoph STEAL the BEST - INVENT the REST |
|
|
|
#2 |
|
diyAudio Moderator Emeritus
Join Date: Jun 2002
Location: U.K.
|
Not enough primary inductance
![]() I think they'll just blow the fuse or seriously overheat.Sorry, |
|
|
|
#3 |
|
diyAudio Member
Join Date: Mar 2003
Location: Haarlem, the Netherlands
|
Probably the core will go into saturation because of the increased number of volt-seconds, causing excessive currents and blown fuses or overheating.
At 50Hz, a transformer with one primary winding intended for 115V, 400Hz should be able to handle 115V*50Hz/400Hz=14.375V without saturation. With two windings in series, you can go up to 28.75V. Not very useful with 230V mains. |
|
|
|
#4 | |
|
diyAudio Member
Join Date: Nov 2002
Location: Netherlands
|
Quote:
Only if you lower your mains 8 times also ![]() 400Hz is/was common on aeroplanes to save weight and these trannies probably come from that area. But these are completely unsuitable for 50/60 Hz, period. Be careful with 50 Hz, they will for sure go into saturation and because these are hermetically canned, will for sure explode with a big bang when given sufficient time, and that can be lethal! Cheers
|
|
|
|
|
#5 | |||
|
diyAudio Member
Join Date: May 2002
Location: Bavaria (south of veal sausage equator)
|
Quote:
that`s what I thought too. But it has still inductance also at a lower level. So when I load them with a (much) lower current than rated I thought it should be possible. Quote:
I wanted to hook up the two primaries in series not secondary windings - so with series connected primaries and 230V I should get about the same secondary voltage as rated for 115V (6,3VAC - for tube filaments). Moreover saturation is current/power dependend and I don`t think voltage ratings alone tell anything about saturation. Quote:
after Your responds it seems to be clear that I can`t use them for what I have them intended but I would be satiesfied with a much lower secondary current rating in order I can use them at all for something else.Do You think it`safe enough when I power one up very slowly with a variac and load it increasingly with an adjustable power resistor while monitoring the temperature of the transformer? For additional safety precaution I could test them outside under some sort of enclosure. Me thinks the temperature should be a good indicator if the transformer is overloaded - isn`t it? If this would be reasonable, what do You think how far up I can go in temperature? Anyway, many thanks for Your help !!!
__________________
Christoph STEAL the BEST - INVENT the REST |
|||
|
|
|
#6 |
|
diyAudio Member
Join Date: Mar 2003
Location: Haarlem, the Netherlands
|
Dear Cocolino,
I'm also talking about primary voltages. A transformer with two 115V, 400Hz primaries connected in series should be able to handle 28.75V of primary voltage at 50Hz (giving the same primary current as 230V, 400Hz). Of course the secondary voltage will then become about 6.3V*50Hz/400Hz=0.7875V. |
|
|
|
#7 |
|
diyAudio Member
Join Date: Jul 2003
Location: Hannover
|
cocolino,
unfortunately you cannot use the 400Hz transformers @50/60Hz without lowering the primary voltage, because the core saturates. With Uind = -dPhi/dt = -L*dB/dt you can see, when you increasing dt by 8 (one eigth of the frequency) you must decrease Uind (=primary voltage) by 8. Because of economical reasons the core is driven near by the saturation Bmax. |
|
|
|
#8 |
|
diyAudio Member
Join Date: May 2002
Location: Bavaria (south of veal sausage equator)
|
Well, it looks like that I can actually forget them completely.
Anyone needs some nice and cheap transformers? Thanks to everybody for the lesson!!
__________________
Christoph STEAL the BEST - INVENT the REST |
|
|
|
#9 |
|
diyAudio Member
Join Date: Oct 2003
Location: Denmark, Viborg
|
Sell them as copper scrap, and buy yourself a "sad experience diminsher" beer for the money.
![]() Magura
__________________
Everything is possible....to do the impossible just takes a little while longer. www.class-a-labs.com |
|
|
|
#10 | |
|
diyAudio Member
|
Quote:
__________________
www.audiosector.com “Do something really well. See how much time it takes. It might be a product, a work of art, who knows? Then give it away cheaply, just because you feel that it should not cost so much, even if it took a lot of time and expensive materials to make it.” - JC |
|
|
![]() |
| Thread Tools | Search this Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| high frequency transformers | ohuzoor | Parts | 3 | 13th April 2009 01:15 AM |
| from 120V 50hz to 230v 50hz? | testarossa2k | Power Supplies | 16 | 13th March 2007 01:32 PM |
| Output transformers and frequency response | dsavitsk | Tubes / Valves | 21 | 3rd December 2006 06:48 PM |
| New To Site? | Need Help? |