Hello,

Does anyone know if AnTek transformers can be used with each secondary winding being used separately. A lot of manufacturers I see say that they either have to be in series or parallel...

I do not see any mention of this on the AnTek datasheets. Do you reckon I could use each secondary winding individually?

I do NOT want to use it as a center tap transformer.

Thanks.
  Reply With Quote
Old 16th March 2012, 03:02 AM   #2
diyAudio Member
 
nigelwright7557's Avatar
 
Join Date: Apr 2008
Location: Carlisle, England
Yes you can.
  Reply With Quote
Old 16th March 2012, 03:06 AM   #3
diyAudio Member
 
Join Date: Jun 2011
Thank you Nigel.
  Reply With Quote
Old 16th March 2012, 03:52 AM   #4
diyAudio Member
 
zigzagflux's Avatar
 
Join Date: Oct 2006
Location: Charlotte, NC
Normally, that recommendation is to ensure the user does not attempt to pull full VA out of 1/2 the primary or 1/2 the secondary windings. The core can handle it, but the individual winding likely cannot (or at least will have much poorer regulation than using both). So to be on the safe side, only load each winding to 1/2 of the total VA. You can use both secondary windings individually, but each winding runs at 1/2VA.
  Reply With Quote
Old 17th March 2012, 05:20 AM   #5
diyAudio Member
 
Join Date: Jun 2011
Thanks. So for example...

Antek - AN-1212

This would be 12v-1 @ 2.1A and 12v-2 @ 2.1A?
  Reply With Quote
Old 17th March 2012, 05:50 AM   #6
diyAudio Member
 
zigzagflux's Avatar
 
Join Date: Oct 2006
Location: Charlotte, NC
No, that's a 100 VA unit, so you can pull 12V-4A out of each winding simultaneously. 12*4=48 VA on each, which is 1/2 the total VA rating of the transformer. The caution is not to try and pull 8A out of one secondary winding, which the copper may not be rated for.

I see in the data sheet they specifically say the copper is oversized, so you probably do have some overload flexibility, but just be aware of the principle.
  Reply With Quote
Old 17th March 2012, 03:00 PM   #7
diyAudio Member
 
Join Date: Jun 2011
Oh I see. Sorry for my ignorance. Well that's good. These transformers are quite cheap actually...

Thanks.
  Reply With Quote

Reply


Hide this!Advertise here!
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Turning a 6.3 V secondary into a 5 V secondary on an Antek 2T350 tomchr Tubes / Valves 30 15th October 2012 02:20 AM
Torodial transformer - help with secondary windings pvh1987 Power Supplies 2 2nd October 2011 07:45 PM
Shorted secondary windings of transformer Edvard Tubes / Valves 5 29th December 2010 11:22 PM
adding and using secondary windings jrenkin Power Supplies 0 19th April 2010 04:05 AM
Parallel secondary windings jlm Pass Labs 6 27th March 2004 11:39 AM


New To Site? Need Help?

All times are GMT. The time now is 11:30 AM.


vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.
Copyright 1999-2014 diyAudio

Content Relevant URLs by vBSEO 3.3.2