![]() The welder is an inverter tig that has a three prong 240 plug. My shop has a three prong 240vac receptacle/service. I attached an image of the operating manual page that describes the power requirements. (the image was too big to upload so here's a link) http://img378.imageshack.us/img378/1...ualpageon5.jpg Inside the welder the green/ground from the 240 service is bolted directly to the chassis. I'm taking 120 switched from one of the legs so that I can turn the cooler on/off with the welders main switch. The cooler I'm making is intended basically to be a semi attached 'auxilliary' unit to the welder. I was afraid this was too elementary a question so I snuck out to an electrician and he told me it was 'electronic' and beyond his ken. But it was his opinion that I could just wire it as I've shown in the diagram and attach both neutral coming into the cooler AND ground from the SMPS to the cooler chassis. I went to an electrical engineer at a plant down the street that manufactures transformers. He scratched his head for a while and admitted that he could not tell me anything certain. I don't know whether to be astonished or demoralized. I asked half a dozen more people ranging from heating and cooling guys, electricians, and in other forums such as this. I got half a dozen more answers. Some said my only option was to rewire the service for a four blade plug and replace the line on my welder so that I had a separate ground and neutral going back to the service box (where they are, naturally, joined together anyway). Only then, it was stated, would I be able to connect my SMPS ground to chassis and true ground, and then the neutral would be 'floating'. Is it really that complicated? I want to be safe. I don't want to damage the SMPS. I don't want to burn my house down. I put in my service and wired my entire home, including this shop. Had it inspected and the inspector praised my work. So why does this stuff seem beyond my (and most others I've asked) comprehension? |
|
|
|
|
#2 |
|
diyAudio Member
Join Date: Nov 2004
|
The following was suggested. Can anyone elaborate on how this is actually implemented? Is it really the only way to go short of rewiring to a four prong outlet?
If you only have a three-prong plug, you must use a transformer with a primary of 240v, and go between L1 and L2. Otherwise, you will be putting current through the ground wire, and there will be voltage on the chassis. Am I energizing the chassis however I choose to ground it the diagram I posted? So if what is stated is true, is my welder then utilizing an interal transformer of the type/application mentioned to keep the current from being put through the ground wire? (that doesn't make sense i know, but i'm just showing how frustrated/confused i am) |
|
|
|
|
#3 |
|
diyAudio Member
Join Date: Sep 2006
|
I hope the only reply comes from a qualified electrician. . .
That think could kill you quick! AndrewT might be the one! or was it Neo. . . |
|
|
|
|
#4 |
|
diyAudio Member
Join Date: Jan 2008
|
Although you could use the ground wire and a hot wire to provide 120V, this is NOT good practice, and would not conform to code, since the ground conductor is not to be used as a current-carrying conductor, it is there for fault protection only.
If the welder has 4-wire service (hot, neutral, hot, ground), go ahead and connect the SMPS to one hot and to neutral. The ground connection for the SMPS would obviously be connected to ground. If the welder does not have a 4-wire service, you only really have two choices. Either get an SMPS that can operate on 240V, or a step-down transformer with 240V primary. Ground must still be connected to ground. |
|
|
|
|
#5 |
|
diyAudio Member
Join Date: Nov 2004
|
I'm trying to understand the idea that the ground is never to be used for current.
This is a brand new model welder from Thermadyne Worldwide. It uses three wires to connect at the receptacle to 240vac using two 120vac wires and a ground. Is it not using that ground inside the machine as the leg to make 120 plus 120 equal 240? I looked into a comparable model from Miller Welding. This years Dynasty 200dx Inverter Tig connects to single phase 240vac in exactly the same manner. How is this machine constructed to a level of acceptable safety adequate to allow it to be sold anywhere in the United States, that I cannot achieve by using the same power source? |
|
|
|
|
#6 |
|
diyAudio Member
Join Date: Jan 2008
|
In 240V single-phase applications, current flows from one HOT wire to the other HOT wire. No current flows in the ground wire.
Some appliances use a neutral wire because they also require a 120V supply on top of the 240V. For example, an oven range might use 120V for the control circuitry and the 120V front panel outlets, a clothes dryer might use 120V for the motor. The arc welder on the other hand might only need 240V supply to it's transformer, thus a neutral connection is not required. |
|
|
|
|
#7 |
|
diyAudio Member
|
If I'm understanding this correctly, you want to wire the 120v water cooler power supply directly to the 240v welder?
If so, you cant do that with what you have currently. As you said, the equipment grounding conductor (green "ground" wire) must never carry any current. The welder manual page you posted is specific about not using a neutral connection. The person who told you you need to re-wire to a 4 wire receptacle was correct. Alternately, you could connect the water cooler setup to a normal 120v receptacle with a standard 3 prong 120v house plug. As an explination, the equipment grounding conductor, commonly referred to as ground, has only one function. That function is to carry return current and pop a fuse/breaker in the event that a voltage carrying conductor (hot leg) shorts to exposed metal. (Or anything else other then the neutral conductor.) This is what keeps you alive if something goes wrong. This is also the reason the equipment grounding conductor is bonded to the neutral at the service enterance. To provide a current path for faults to ground back to the neutral to blow the fuse/breaker. Current on the EGC (ground) gives I^2R losses along the conductor, locally elevating the voltage of the grounded equipment above all the other grounded equipment. Touch this mis-wired piece of equipment, along with another piece of equipment not on the same outlet, and you may be killed. Now I'm not a licensed electrician, however I do have the 2008 national electrical code sitting next to me, which I have read and mostly understand. As such, I disclaim any and all responsability if your house burns down or you kill yourself. Not that I remotely expect it to with the advice I have given you, but just in case. -Edward |
|
|
|
|
#8 |
|
diyAudio Member
Join Date: Jan 2008
|
Current does NOT flow in the neutral conductor, if you look at another post on here titled 'How to connect gnd' in the Chip-AMp section and the thread was started by samsagaz. I have put a simple drawing (at/near the bottom of the thread) showing how electricity is generated (3 Phase) and you will see that the Neutral and Earth both come from the same point in the generating set, this is called the 'Star Point'
To prove that electricity does not flow in the neutral, AND PLEASE DO NOT TRY THIS AT HOME, when I install Single or Three Phase boards, when every circuit is switched on you can touch the Neutral bar with your finger and you will not get electrocuted. Again DO NOT TRY THIS AT HOME, as you cannot guarantee that you main supply is perfect. By the way some boards I install run at 250Amps @ 400v. Which is one hell of a lot of power and WILL KILL YOU. If your welder needs 240v then you would need to step-up the supply voltage over in America from 120Vac to 240Vac using a Step-Up Transformer. To switch both at the same time you will need an interlinked (not electrically but mechanically) double pole switch that is rated above 230v, get a 400v switch to ensure that the insulation does not break down, welders draw lots of power, and give them their own supply, one at 230 and the other at 120v. The double-pole interlinked switch does not (ever) switch your earth. An alternative to using this type of switch would be to use either relay or contactor switching. The contactor method is the safest and the one that I would go for, but really there are a number of ways to achieve what you are looking for. Both Earth's, the one in the welder and the one in your cooler need to both be connected to supply earth for compliance with regulations. Gareth (BS 7671 Qualified Electrician) PS....Please, Please, Please do not fool around with mains electricity under the right conditions 30mA is enough to kill. Again ELECTRICITY KILLS |
|
|
|
|
#9 |
|
diyAudio Member
Join Date: Jan 2008
|
I think you're thinking the wrong way about North-American household power distribution. Power to a household is supplied from 3 wires, two labeled as "hot" and 1 the "neutral". The neutral is actually the center-tap of the pole transformer, with the hot wires being each end of the winding. From the center-tap to either end the voltage is 120 volts. End to end (hot to hot) the voltage is 240V.
As such, power outlets and circuits can be wired as either 120V or 240V, or both (4 prongs). 120V circuits in breaker panels are set up in such a way that the load on each hot wire is more or less balanced. For 120V circuits, current flows through 1 hot wire and the neutral (center tap). A typical household has a majority of 120V appliances, mostly low-powered. High-powered appliances such as oven ranges, hot water heaters, and space heaters operate on 240V. |
|
|
|
|
#10 |
|
diyAudio Member
Join Date: Nov 2004
|
I did realize after I posted that I'd misapprehended something. I had thought that the hot wires used the ground to complete. I measured across both hot wires and indeed got 240.
It looks like the avenue I'm seeking is to use a transformer off of the two hot legs (240) and step it down to 120v. Now I can use the ground to connect to the chassis of this project. This presents a new challenge. I've spent a couple of months in the shop painstakingly paring off pounds and inches from this thing and it is now the size of a large brick. I have a space approx 4 x 2 x 2.5 inches left in it to accomplish transforming 240 to 120 for use by my switch mode power supply and a small electric pump. Any recommendations? After all this work I hate like hell contemplating an 8 x 8 x 8 inch separate power supply. Even a stacked core transformer is going to set me way back in weight and bulk. |
|
|
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
|
|
|
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Parallel LM3886, input ground, power ground, safety resistor and oscillations. | markiemrboo | Chip Amps | 5 | 9th August 2007 03:50 PM |
| Chassis Ground = Circuit Ground --> Problems? | rhildenbrand | Pass Labs | 5 | 23rd April 2004 01:08 AM |
| does connecting mains ground with circuit ground create a ground loop? | jarthel | Everything Else | 0 | 25th June 2003 12:55 PM |
| Should I directly connect my signal ground to chassis ground? | Bricolo | Solid State | 3 | 28th February 2003 05:31 PM |
| New To Site? | Need Help? |
| Page generated in 0.13421 seconds (83.64% PHP - 16.36% MySQL) with 11 queries |