I've replaced the faulty electronic ballast in an old commercial projector with a magnetic ballast. The PJ uses a 575W MH lamp, which works fine on the 400W ballast.
Does anyone know if it would be OK to run a 150W ballast in parallel with the 400, in order to obtain more light output? I'd leave the igniter connected to just the 400, as the lamp starts fine as it is. I know that some commercial lighting installations do use parallel ballasts, but they are usually of equal rating. I only have one lamp at present (hoping to get another soon, though) so I don't want to risk damaging it by uninformed experimenting.
__________________
"I never did care for music much; It's the high fidelity!" Flanders & Swann |
|
|
|
#2 |
|
diyAudio Member
Join Date: Mar 2004
Location: Shropshire, England
|
Anyone?
__________________
"I never did care for music much; It's the high fidelity!" Flanders & Swann |
|
|
|
#3 |
|
diyAudio Member
Join Date: Oct 2005
|
no clue sorry
|
|
|
|
#4 |
|
diyAudio Member
Join Date: Jul 2005
Location: Colorado
|
Theoretically it's possible. But, ensuring that all the components are set up properly and that they can handle all the current, I'm guessing, would be a nightmare.
|
|
|
|
#5 |
|
diyAudio Member
Join Date: Dec 2005
Location: Louisiana
|
i would not suggest trying it.... they're not made to be run like that and probuably couldn't handle the extra wattage
__________________
15.4" eMachines LCD(1024 x 768) 3M 9700 OHP Optics in custom enclosure 2 Fan Cooling Setup Works Great! |
|
|
|
#6 |
|
diyAudio Moderator
Join Date: Apr 2002
Location: Chatham, England
|
They won't share the load properly, one will likely hog all the current and go bang...
__________________
Al The miracle is not to fly in the air, or to walk on the water; but to walk on the earth. Chinese Proverb |
|
|
|
#7 |
|
diyAudio Member
Join Date: Mar 2004
Location: Shropshire, England
|
Thanks for the replies.
There are diagrams in my rather ancient Philips lighting handbook showing discharge lamps running on paralleled standard 'half the wattage' ballasts, so presumably there's no problem with current sharing that way. My thinking is that as the igniter will be run from the 400W ballast, the lamp can only strike by drawing current through that ballast. The 150W one will supply the additional current to allow it to run at (nearly) full power. Since, as far as I understand it, the lamp is virtually a short circuit once the arc is struck, the current through each ballast is limited by the impedence of the ballast itself, so the ballast can't be damaged by overcurrent. Please point out the flaws in my arguement
__________________
"I never did care for music much; It's the high fidelity!" Flanders & Swann |
|
|
|
#8 |
|
diyAudio Member
Join Date: Dec 2005
Location: Louisiana
|
well, give it a shot, be careful, and if you don't die and a ball of fire, post your results with some before and after pics :P
__________________
15.4" eMachines LCD(1024 x 768) 3M 9700 OHP Optics in custom enclosure 2 Fan Cooling Setup Works Great! |
|
|
|
#9 |
|
diyAudio Member
Join Date: Sep 2004
Location: Vista, CA
|
With identical ballasts, their phase characteristics would match. With different ballasts, they may not. That might not matter, in terms of over-working one ballast or the other. But it might send the lamp a novel waveform.
On the other hand, electronic ballasts don't try to mimic magnetic ballast waveforms at all. They just use square waves and integrate to get the average power per cycle. So a novel waveform should not matter much. Maybe the non-ignitor-connected ballast will prevent the lamp from starting by swallowing the high voltage pulse? You might have to start it with the 400 Watt ballast, and then switch in the 150 Watt. Let us know. |
|
![]() |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| fluorescent light ballasts | sorenj07 | Parts | 9 | 7th November 2006 04:34 AM |
| Fluorescent ballasts in SE | Jaime | Tubes / Valves | 1 | 30th January 2006 08:07 PM |
| New To Site? | Need Help? |
| Page generated in 0.16556191 seconds (82.69% PHP - 17.31% MySQL) with 10 queries |