Old 8th November 2012, 02:51 PM   #1
evanc is offline evanc  United States
diyAudio Member
 
Join Date: Sep 2009
Location: New Jersey. About 1 hour from NYC and 1 min. from the beach
Default Generator question

So after 11 days in the dark and cold and reports of 10more days I need some advice. My forced hot air gas furnace is relatively new and has a computer board in it. I have been warned not to hook my old job site generator to the furnace for fear of damaging the computer. The generator has plenty of wattage to do the job.

Are these concerns valid? If so what do I need to do to run my furnace off this generator?

Would a good sized inverter...car battery....charger....generator be ok? If so how big an inverter do I need?

Sorry for so many questions, but I know for this kind of advice this is the place to be.
Thanks from the jersey shore...Evan
__________________
http://www.evancotler.com
  Reply With Quote
Old 8th November 2012, 04:21 PM   #2
diyAudio Member
 
Osvaldo de Banfield's Avatar
 
Join Date: Dec 2011
Location: Barrio Garay,Almirante Brown, Buenos Aires, Argentina
I think that no problem would be if the generator has power and voltage corresponding to the oven you are wanting to wire to it. Computer must be SMPS or transformer isolated from the supply, so if it has a rare waveform (not too sine), the CPU will never know it.

Are you damaged from Sandy?? Lament if it is true!

Salu2.
__________________
LW1DSE
  Reply With Quote
Old 8th November 2012, 04:27 PM   #3
diyAudio Member
 
kevinahcc20's Avatar
 
Join Date: Apr 2009
Location: Farmington Hills, MI USA
Check the furnace before you hook up to determine how the control module is wired. Chances are that the control module is powered off a DC supply fed by the 120VAC mains to the furnace. If so I would expect the DC supply to provide any needed isolation from noise, etc on the mains supply. If I had been in the cold for 11 days I'd likely be taking the chance.
__________________
Kevin(ahcc20)...I'd rather have a bottle in front of me than a frontal lobotomy!
  Reply With Quote
Old 8th November 2012, 04:27 PM   #4
diyAudio Member
 
Frank Berry's Avatar
 
Join Date: Sep 2003
Location: Midland, Michigan
The generator should run your furnace just fine.
__________________
Frank
  Reply With Quote
Old 8th November 2012, 04:34 PM   #5
evanc is offline evanc  United States
diyAudio Member
 
Join Date: Sep 2009
Location: New Jersey. About 1 hour from NYC and 1 min. from the beach
Thanks for the replies. We have a wood stove in the living room that is now also the bedroom for the 4 of us. The temps are mid 50s f overnight. Not too bad, at least I have a house to heat. If the furnace worked I could get out longer without worrying about the house getting cold during the day and not being able to warm it up before nightfall. Also I believe it would give my wife an emotional lift to hear the furnace fire up.
Thanks, Evan
__________________
http://www.evancotler.com
  Reply With Quote
Old 8th November 2012, 11:32 PM   #6
Enzo is offline Enzo  United States
diyAudio Member
 
Join Date: Sep 2004
Location: Lansing, Michigan
Be careful, make sure to isolate the furnace connections from the rest of the house wiring, otherwise the generator will try to power the whole house back through the service panel. And if the power grid outside should come back online wwhile you are generating, something will blow.
  Reply With Quote
Old 8th November 2012, 11:35 PM   #7
freax is offline freax  Australia
diyAudio Member
 
freax's Avatar
 
Join Date: Sep 2007
Location: NSW
I've been researching this a little bit, and I've picked up the advice from someone else that putting a 60w-100w incandescent or halogen light load onto the generator wired in parallel to your furnace will give the generator a steady load, and won't result in the generator stomping on its choke or throttling up to compensate for a heavier load.

But this is all relative to the load that the furnace is going to put onto your generator, and the size of your generator, can we get some further information about your setup there?

You say the generator has plenty of wattage to do the job, how much is it?

Whats the wattage of your furnace fan?

You mention an inverter, NO! if its a modified sine wave inverter then NO don't use it!!, if its an extremely expensive $1000 pure sinewave inverter then yes it might work, but be very careful of manufacturers stating that an inverter is a pure sinewave when infact its not! If it says "pure" on the inverter then thats not a good sign!

If the furnace has a mains powered fan in it then this WILL burn out when run from a modified sinewave inverter...
__________________
"It seems that perfection is reached not when there is nothing left to add, but when there is nothing left to take away" - Antoine de Saint Exupéry

Last edited by freax; 8th November 2012 at 11:37 PM.
  Reply With Quote
Old 9th November 2012, 12:30 AM   #8
tvrgeek is offline tvrgeek  United States
diyAudio Member
 
Join Date: Dec 2009
Location: Md
A nice big line filter would not hurt.
  Reply With Quote
Old 9th November 2012, 12:30 AM   #9
evanc is offline evanc  United States
diyAudio Member
 
Join Date: Sep 2009
Location: New Jersey. About 1 hour from NYC and 1 min. from the beach
The generator is 8k watt running and 13k startup. I knew to disconnect from the panel for the line mans safety. I tried it and the furnace doesn't work powered from his generator. The computer controlling the furnace has 2 LEDs that can flash diagnostic codes. I get a code that is not listed on the little chart in the furnace. Worth a try, but I couldn't make it work.
Evan
__________________
http://www.evancotler.com
  Reply With Quote
Old 9th November 2012, 12:47 AM   #10
tvrgeek is offline tvrgeek  United States
diyAudio Member
 
Join Date: Dec 2009
Location: Md
Mine works fine. Processor controlled Carrier 89% type.

Do you ground your generator chassis? Actually required by code.
  Reply With Quote

Reply


Hide this!Advertise here!
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Audio generator question tttoan Equipment & Tools 6 12th June 2012 12:01 AM
Signa Generator domtweaker Swap Meet 0 7th February 2012 07:26 AM
Signal Generator: Which one to buy ? What to look for in a signal generator ? HP8903B Tubes / Valves 45 12th January 2012 09:01 PM
Function Generator riverrat373 Equipment & Tools 12 17th February 2010 08:41 AM
Signal Generator Help Bengali Equipment & Tools 12 24th April 2008 04:20 PM


New To Site? Need Help?

All times are GMT. The time now is 07:02 AM.


vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.
Copyright ©1999-2014 diyAudio

Content Relevant URLs by vBSEO 3.3.2