Old 6th March 2011, 08:45 PM   #1
diyAudio Member
 
Join Date: May 2010
Location: South East USA
Default Isolation Transformer (multi-winding transformers)

I have 2 identical unknown transformers that I'd like to wire back to back to make an isolation transformer. They are both from the same model UPS (battery back up) and I haven't been able to find ANY information on them (markings include 430-2060B; E184736; DV-130-1). Since they are the same, I'm not worried about getting a 1:1 ratio. My question is, can I hook up all the different windings back to back, or should I just use a single winding? I haven't measured the voltages yet, but I have 3 large wires on the output side that are Red, White, and Black. My thought is: MAINS (110v) ---> xfmr1 Input --- xfmr1 Red Output ---> xfmr2 Red Input --- xfmr1 White Output ---> xfmr2 White Input --- xfmr1 Black Output ---> xfmr2 Black Input --- xfmr2 Output (110v)

Does this sound right?
Thanks!
  Reply With Quote
Old 6th March 2011, 09:46 PM   #2
diyAudio Member
 
Join Date: Nov 2008
Draw a pix.
Transformers are not 100% efficient. You will loose 10% ore mor of the voltage (depending on the load) on the output of your contraption. E
  Reply With Quote
Old 6th March 2011, 10:34 PM   #3
expert in tautology
diyAudio Member
 
bear's Avatar
 
Join Date: Apr 2002
Location: New York State USA
Hmmmm... interesting to think about.

It should work IF you get the phase correct.

You might get some bucking because of slight phase differences between the sets of windings. That being due to the variance in inductance and interwinding capacitance.

I'd fire it up first with just the heaviest windings connected, and use a LOW voltage xmfr as the source (like 12vac) and see what the output looks like compared to the input. Then try it the same way with the rest of the windings. Finally, try it with some sort of current limiting (a lightbulb for example - or a variac with ammeter) on full mains power.

I doubt that any voltage will be lost, but some power may be eaten up in the xfmrs, but who cares...

_-_-bear
__________________
_-_-bear
http://www.bearlabs.com -- Btw, I don't actually know anything, FYI -- [...2SJ74 Toshiba bogus asian parts - beware! ]
  Reply With Quote
Old 7th March 2011, 04:58 PM   #4
diyAudio Member
 
Join Date: May 2010
Location: South East USA
MM, Here is a hastily drawn diagram in Paint. I'm not too worried about voltage loss, as this will be (Before???, After???) my variac.

Bear, I'm not sure which windings are the heaviest, as all three wires shown are the same gauge. Could it be center-tapped? If so, would it damage anything if hooked up as shown in the diagram?

Thanks Moose and Bear! Lot's of animals around these parts....
Attached Images
File Type: jpg IsoDiagram.JPG (20.6 KB, 300 views)
  Reply With Quote
Old 7th March 2011, 06:20 PM   #5
diyAudio Member
 
Join Date: Nov 2008
Asumptions: You know which side is the 110 volt and that the 2 xformers are the same model, than you can figure out what should go where. I would not use the centre (I spell that the Canadian way) tap of the secondary. E
  Reply With Quote
Old 8th March 2011, 05:00 PM   #6
diyAudio Member
 
Speedskater's Avatar
 
Join Date: Sep 2002
Location: Lakewood, Ohio
Are UPS transformers wound the same way that typical linear power supply transformers are?
__________________
Kevin
  Reply With Quote
Old 9th March 2011, 02:09 PM   #7
diyAudio Member
 
Join Date: Nov 2008
On the input of a UPS you most likely have a HF switching supply to charge a battery. The core would be a powder-iron design. On the out you could find a ferro-resonant transformer. And than, maybe not. E
  Reply With Quote
Old 10th March 2011, 12:17 AM   #8
diyAudio Member
 
Join Date: May 2010
Location: South East USA
So I finally had a chance to actually test the transformers in question. Both tested the same, and all results were at 60hz with 110V in.

Red-White: 15.7vac
White-Black: 7.85vac
Red-Black: 7.85vac

Blue-Brown: 19vac

I didn't mention the blue/brown wires before as they are quite small compared to the rest so I'm not planning on using them no matter what.

So what's up with different values between the first three sets of wires? Can I still use this as an isolation setup? Help and thanks!
  Reply With Quote
Old 11th March 2011, 08:59 PM   #9
Spiny is offline Spiny  United Kingdom
diyAudio Member
 
Spiny's Avatar
 
Join Date: Feb 2008
You have a 7.5-0-7.5 volt transformer I guess allowing for mains variations (otherwise a 0-15 volt with a centre tap - same thing)

connect the red and white on one to the red and white on the the other and insulate the centre tap wires.
That will work fine. Will work as back to back transformers at the full power rating
  Reply With Quote
Old 16th March 2011, 11:57 PM   #10
diyAudio Member
 
Join Date: May 2010
Location: South East USA
Spiny, thank you! That worked! I measured 110vac in and just a little less on the output (with 2 multimeters).

Next question, can I (or do I want to) connect the smaller wires in the same way to get a little extra capacity? Seems a shame to have an unused coil just going to waste.

Thanks!
  Reply With Quote

Reply


Hide this!Advertise here!
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Winding Your Own Transformers tmblack Power Supplies 9 10th April 2010 08:02 AM
FREE! Two 7 KV (!) isolation transformers (Signal Transformer) for balanced power. markmaloof Swap Meet 0 22nd January 2010 08:15 PM
Two 7.5 KV (!) Signal Transformer Isolation transformers, only $200, NYC markmaloof Swap Meet 2 12th July 2007 12:47 AM
Isolation transformers Bricolo Parts 36 28th June 2004 07:46 PM


New To Site? Need Help?

All times are GMT. The time now is 02:44 AM.


vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.
Copyright 1999-2014 diyAudio

Content Relevant URLs by vBSEO 3.3.2